    When installing branch circuits for artificial bodies of water, such as municipal infrastructure, what is the minimum size (copper) equipment grounding conductor required for a 15A, 120V circuit?
    A) 14 AWG
    B) 12 AWG
    C) 10 AWG
    D) 8 AWG
    Answer: B
    Article 682 applies to the installation of electrical wiring for natural or artificially made bodies of water not covered by other Articles in the Code. Under normal circumstances, a 14 AWG (copper) equipment grounding conductor would be acceptable as per Sec. 250.122. However, as specifically noted in Sec. 682.31(A), the EGC shall not be smaller than 12 AWG.