Code Quiz: Load Side Utilization Conductor Size in Low-Voltage Suspended Ceiling Power Distribution System
NEC requirements for load side utilization conductor size in low-voltage suspended ceiling power distribution system
July 21, 2016
What is the minimum size (copper) current-carrying conductor permitted for load side utilization equipment of low-voltage suspended ceiling power distribution systems?
A) 18 AWG
B) 16 AWG
C) 20 AWG
D) 24 AWG
Answer: D
The construction specifications for the sizes and types of conductors of low-voltage suspended ceiling power distribution systems are outlined in Sec. 393.104 of the 2014 NEC. As noted in 393.104(A), “current-carrying conductors for load side utilization equipment shall be copper and shall be 18 AWG minimum.” However, there is an Exception to this rule. The Exception states:
“Conductors of a size smaller than 18 AWG, but not smaller than 24 AWG, shall be permitted to be used for Class 2 circuits. Where used, these conductors shall be installed using a Chapter 3 wiring method, shall be totally enclosed, shall not be subject to movement or strain, and shall comply with the ampacity requirements in Table 522.22.”