Code Quiz: Hoistway Door Interlock Wiring
Hoistway Door Interlock Wiring and the NEC
When installing conductors for hoistway door interlock wiring, the conductors shall be ___________________.
A) flame retardant and suitable for a temperature of not less than 200°C (392°F) and type SF or equivalent
B) physically protected using an approved method such that the conductor assembly is flame retardant and suitable for a temperature of not less than 200°C (392°F)
C) either A or B above
D) any 90°C rated conductor
Scroll Down to See the Answer
Answer: C
As outlined in Sec. 620.11(A), when installing conductors for hoistway door interlock wiring, the conductors shall be flame retardant and suitable for a temperature of not less than 200°C (392°F) and type SF or equivalent, or physically protected using an approved method such that the conductor assembly is flame retardant and suitable for a temperature of not less than 200°C (392°F).