Question: Where are you required to make the connection between the equipment grounding conductor (EGC) and the neutral conductor at a 208/120V, 3-phase, four-wire service?
See the answer below.
Answer: Within the service disconnect enclosure.
Explanation: Section 250.24(B) requires the main bonding jumper to connect the EGC and the service disconnect enclosure to the neutral (grounded conductor) within the enclosure.