Question: The main circuit breaker of a 2,500A 480/277V three-phase, four-wire service needs to be replaced. Can a reconditioned circuit breaker be used for this application?
See the answer below.
Answer: No
Explanation: The 2020 NEC added a new section (210.15) for reconditioned equipment. This section specifically prohibits the reconditioning of the following equipment:
(1) Equipment that provides ground-fault circuit-interrupter (GFCI) protection for personnel
(2) Equipment that provides arc-fault circuit-interrupter (AFCI) protection
(3) Equipment that provides ground-fault protection of equipment
Because the service listed in the question meets the requirements of Sec. 230.95, GFCI protection of equipment is required and the new requirements of Sec. 210.15 would prohibit the use of a reconditioned circuit breaker.