Based on the 2020 NEC.
True or False?
Question: Branch-circuit conductors serving a single air conditioning compressor are required to be sized not smaller than the branch-circuit selection current.
See answer below.
Answer: False
Explanation: The branch-circuit conductors are required to be sized at a minimum of 125% of either the motor-compressor rated-load current or the branch-circuit selection current, whichever is greater. In the 2020 NEC, Sec. 440.32 was revised to make it clear that the 125% applied to both motor-compressor rated-load current and the branch-circuit selection current not just the motor-compressor rated-load current.
Lupacchino is a senior design engineer with Gaylor Electric, Inc. in Noblesville, Ind. and serves as an alternate on NEC Code-Making Panel No. 3. He is currently licensed in more than 80 jurisdictions. He can be reached at [email protected].