Code Quiz: Grounding Electrode Conductors and Weep Holes
Based on the 2026 NEC.
Question: True or false? Installation of a grounding electrode conductor through a weep hole in the bottom of a disconnect switch is permitted.
See answer below.
Answer: False
Reference: Section 250.64(G)
Explanation: Article 250.64(G) prohibits installation of grounding electrode conductors through ventilation openings, a change in the 2026 edition of the NEC now adds mounting and drainage openings as prohibited as well. Although not intended to be utilized for this purpose, weep holes are commonly used to route grounding electrode conductors. This practice is now clearly prohibited.
Lupacchino is a senior design engineer with Gaylor Electric, Inc. in Noblesville, Ind. and serves as an alternate on NEC Code-Making Panel No. 3. He is currently licensed in more than 80 jurisdictions. He can be reached at [email protected]
John Lupacchino
Senior Design Engineer