This Violation is “Grounds” for Removal

The most obvious violation here is the way in which the equipment grounding conductors are connected to a piece of wood instead of being connected to the metal box. Section 314.4 requires metal boxes to be grounded in accordance with Art. 250. I can’t see any bonding or grounding connections to the box. Section 250.86 requires this enclosure to be connected to an equipment grounding conductor. Sections 250.110(1) through (6) also require exposed, normally noncurrent-carrying metal parts enclosing conductors that are likely to become energized to be connected to an equipment grounding conductor under certain conditions, including (2) where located in damp or wet locations and (5) where using a wiring method that provides an equipment grounding conductor.

As for the smaller box on the left, I’m not so sure that it’s suitable to be used in a wet location. Section 314.15 requires this box to be placed or equipped so as to prevent moisture from entering or accumulating inside of it. It also requires this box to be listed for use in a wet location. This enclosure appears to be a Type 1 General Purpose enclosure as indicated by Table 110.28. A Type 3 or 3R enclosure would be more appropriate in this specific location.

This Installer Must Have “Spaced” Out

These NM cables will be in harm’s way if they remain secured in this manner. When the sheetrock installer starts securing the wallboard to the furring strips, he could easily damage the cables with a sharp tip if he is slightly off center with the placement of his screws. This is why Sec. 300.4(D) requires these cables to be spaced at least 1¼ in. from the nearest edge of the furring strip where nails or screws are likely to penetrate. This rule is applicable in both exposed or concealed locations where cables or raceway wiring methods are run parallel to framing members such as joists, studs, rafters, and furring strips.

Where the 1¼-inch spacing cannot be maintained, a steel plate or sleeve must be used to provide protection for the cables or raceways. The steel plate must be at least 1/16 in. thick or — according to Exception No. 3 — a thinner plate could be used if it provides equal or better protection and is listed an marked. Exception No. 1 removes the protective sleeves or plates requirement for RMC, IMC, RNC, or EMT.

In violation of Sec. 334.30, a piece of scrap wire was used as the means to secure the cables to the furring strip.

About the Author

Russ LeBlanc

Russ LeBlanc

Owner

Russ started in the electrical trade as an apprentice in 1985. He worked his way up to become a Journeyman Electrician and then eventually became a Master Electrician and Licensed Construction Supervisor. In 1999 Russ become an Electrical Instructor for The Peterson School of Engineering in Massachusetts where he developed his passion for teaching, and quickly became Department Head of Electrical Instruction. Russ has taught thousands of apprentices, electricians, engineers, inspectors, and other electrical professionals during his career as an instructor. He continues to provide electrical professionals with Electrical Code seminars, Arc-Flash Awareness training seminars and educational material through his LeBlanc Consulting Services in North Reading, MA whose specialty is educating electricians. He has been an active member of the NFPA Electrical Section and has authored hundreds of National Electrical Code proposals and comments which have become Code rules to improve the safety for the electrical industry. Russ is also an IAEI certified Electrical Inspector.

Please visit www.russleblanc.net for more information.