Separation Anxiety

A close look at the top left portion of this enclosure reveals the Code violations with this mineral-insulated (MI) cable installation. The installer brought each conductor into this steel enclosure through an individual opening without complying with the requirements in Sec. 300.20(B).When single conductors carrying alternating current pass through magnetic metal such as steel, the effects of induction shall be minimized by either cutting slots in the metal between the individual openings through which the individual conductors pass, or by passing all of the conductors through an insulating wall large enough for all of the conductors of the circuit. One common method installers use is to cut one large hole in the steel wall and then attach a nonmagnetic brass plate to the enclosure and then pass the conductors through this brass plate. This installer followed another path. He drilled holes in the enclosure for two of the conductors and then connected the other two to a separately attached steel plate with individual holes. Even the locknuts on the MI cable connectors are noncompliant magnetic steel. For low-current installations, the inductive heating effects will not be too severe. For higher currents, however, there could be significant heating of the metal between the individual conductor entries.

Weatherproof Woes

I spotted this violation during a recent lunch date with my wife at a popular lobster pier. The outdoor vending machines were plugged into receptacles where the box covers were permanently flipped opened. The receptacle box is installed under a very small overhang, but I would still consider this a wet location rather than a damp one. A driving or beating rain could easily soak these receptacles. For 15A or 20A, 125V or 250V receptacles installed in wet locations, Sec. 406.9(B)(1) requires “an enclosure that is weatherproof whether or not the attachment plug cap is inserted.” This enclosure is only weatherproof when nothing is plugged into the receptacles and the covers are closed. There is an exception allowing “an enclosure that is weatherproof when the attachment plug is removed” for areas subjected to routine high-pressure spray washing, but that exception would not be applicable here. For both wet and damp locations, Sec. 406.9 requires these receptacles to be a listed weather-resistant (WR) type. Section 210.8(B)(4) requires GFCI protection for these receptacles. At present, there are no requirements for using tamper-resistant (TR) type receptacles here, but the ever-increasing requirements in Sec. 406.12 are subject to future changes.

About the Author

Russ LeBlanc

Russ LeBlanc

Owner

Russ started in the electrical trade as an apprentice in 1985. He worked his way up to become a Journeyman Electrician and then eventually became a Master Electrician and Licensed Construction Supervisor. In 1999 Russ become an Electrical Instructor for The Peterson School of Engineering in Massachusetts where he developed his passion for teaching, and quickly became Department Head of Electrical Instruction. Russ has taught thousands of apprentices, electricians, engineers, inspectors, and other electrical professionals during his career as an instructor. He continues to provide electrical professionals with Electrical Code seminars, Arc-Flash Awareness training seminars and educational material through his LeBlanc Consulting Services in North Reading, MA whose specialty is educating electricians. He has been an active member of the NFPA Electrical Section and has authored hundreds of National Electrical Code proposals and comments which have become Code rules to improve the safety for the electrical industry. Russ is also an IAEI certified Electrical Inspector.

Please visit www.russleblanc.net for more information.

Sign up for our eNewsletters
Get the latest news and updates

Voice Your Opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!