NFPA 70E Tip: How Much Maintenance Is Enough For Safety?
Many years before safety-related maintenance requirements made it into NFPA 70E, presenters at conferences for the electrical testing industry asserted that if you didn’t have the maintenance history on a piece of equipment, you must assume the equipment is not in a safe condition. And you must approach the testing process with that in mind.
During Q&A sessions, this assertion would be challenged as paranoid or costly. Or a testing firm project manager would say something like, “I can’t tell my clients how to maintain their plant.” A reply such as, “Actually, you can,” would be followed by a discussion of why unmaintained equipment is unsafe equipment, and you have an obligation to make the job as safe as practical for your employees or to walk away from it.
Chapter 2 of NFPA 70E provides the requirements. It’s a short chapter consisting of 11 short articles. Each of these provides enough basic information for a qualified person to see the bright red line where safe meets unsafe.
Some key points:
- Equipment should be maintained per manufacturer’s instructions and/or industry standards [205.3]. For example, the manufacturer recommends lubricating a breaker mechanism annually based on the conditions of service but this is excluded from the maintenance procedure entirely. You must assume this breaker will not operate properly. Note that dried out lubrication is the No. 1 cause of breaker malfunction.
- Flexible cords and cables must be free of wear or other defects [205.14]. This includes cords and cables integrated with the equipment; don’t confine your thinking to portable cords.
- Covers must be in place [215.1] and raceways and cable trays must be in good mechanical condition so they provide protection and support for conductors [215.3]. If you walk into a facility and see covers missing half their bolts or not even installed, assume maintenance has been zero. The same goes for raceway that is falling apart.
- Fuses must be free of breaks or cracks in their cases, ferrules, and insulators [225.1]. Fuse clips and fuseholders should have enough grip to securely hold the fuses. If you see anything that is cracked, broken, or bent, you are looking at a safety problem resulting from lack of maintenance.