Electrical Troubleshooting Quiz - June 23, 2015
Recently, your factory got a new plant manager. He’s a micromanager and is trying to cut maintenance costs. He told the plant engineer to eliminate insulation resistance (IR) testing for motors because motors fail anyway so the testing is pointless. He also said to lay off two people due to the decreased workload.
Wanting to save the IR program, the plant engineer gave you a list of 10 failed motors and asked you to explain IR testing for each one.
What should be your strategy for preparing a report?
Rather than examine 10 specific instances of failure, it would be better to prepare a short report that explains IR testing. IR testing doesn’t tell you how healthy insulation is (it can tell you if insulation has faulted). But if you perform IR testing frequently enough and trend the results, you’ll get a predictive tool.
Insulation degrades over time, so its resistance slowly decreases. Close to the point of breakdown, the resistance loss accelerates; this produces a downward break in the slope of the plotted line. Because it dries the windings, you should always perform IR testing before performing other tests that require higher voltage.
