Ecmweb 3511 506ecm30pic1x

Illustrated Catastrophes

June 1, 2005
As usual, never consider the following commentary associated with these photos as a formal interpretation of the National Electrical Code (NEC). Without criticizing anyone or any product, the following scenarios present us with serious safety questions. All references are based on the 2005 NEC. JUST TRY TO BLOW THIS Doug Kidd, P.E., Kincaid*Bryant, Lynchburg, Va., found this installation recently

As usual, never consider the following commentary associated with these photos as a formal interpretation of the National Electrical Code (NEC). Without criticizing anyone or any product, the following scenarios present us with serious safety questions.

All references are based on the 2005 NEC.



JUST TRY TO BLOW THIS “FUSE”

Doug Kidd, P.E., Kincaid*Bryant, Lynchburg, Va., found this installation recently while designing a chiller replacement at a state college. He noted that the original installation was completed in 1985 as a part of a major building renovation. The design used a 2,000A high-pressure contact main switch in the switchboard as the building service disconnect. “Maybe the electrician was in a hurry to get temporary power to the building,” Kidd wrote.

In addition, he noted that only three parallel sets of 500 kcmil were used for the service lateral. “That's all the electrician installed,” he said. “Needless to say, we advised the owner to immediately replace the ‘fuses,’ and we added a new service lateral to the existing design.”

These wires are surely not devices — they're not even solid wires. Per 240.2 of the 2005 NEC, a current-limiting overcurrent protective device is “a device that, when interrupting currents in its current-limiting range, reduces the current flowing in the faulted circuit to a magnitude substantially less than that obtainable in the same circuit if the device were replaced with a solid conductor having comparable impedance.”




CONDUCTORS REDUCED TO PAINT COATED PROTECTION

The owner of this facility wouldn't agree to repair this chlorine-damaged conduit, despite the fact that it's located in the pool area and is accessible to guests. There's a good chance the integrity of the ground system has been compromised by this corrosion. The second photo shows how badly deteriorated the remaining portion of the conduit system is in.

Per 300.6(A)(3), “Ferrous metal raceways, cable armor, boxes, cable sheathing, cabinets, elbows, couplings, nipples, fittings, supports, and support hardware shall be permitted to be installed in concrete or in direct contact with the earth, or in areas subject to severe corrosive influences where made of material approved for the condition, or where provided with corrosion protection approved for the condition.”

Found a Code violation? E-mail your photos to Joe Tedesco at [email protected].

About the Author

Joe Tedesco

Tedesco served the industry in many roles during his career. He was a director, senior electrical code instructor for National Technology Transfer, Inc. and American Trainco, Inc.. He was also a codes, standards and seminar specialist for the International Association of Electrical Inspectors and an electrical field service specialist for the National Fire Protection Association in Quincy, Mass. He ran his own business as an NEC consultant and is a Massachusetts licensed master electrician and journeyman electrician and certified electrical inspector (one and two family 2A; General 2B, and Plan Review, 2C). Tedesco also wrote articles for CEE News and EC&M (Code Violations Illustrated and What's Wrong Here?) for more than 15 years and helped launched the Moving Violations video series.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.