A Pole with No Hole

Trust me when I say the view from this side of the pole is the same as the others. The question we need to ask ourselves is what happened to the handhole on this luminaire pole? Was it missing from the start, or did it disappear during a modification process? Whatever the reason, the lack of a handhole is a violation of 410.30(B) of the 2011 NEC.

As noted in 410.30(B)(1), “A pole shall have a handhole not less than 50 mm × 100 mm (2 in. × 4 in.) with a cover suitable for use in wet locations to provide access to the supply terminations within the pole or pole base.” An Exception states no handhole shall be required in a pole less than 8 ft tall. However, this pole greatly exceeds that height limit. Another Exception says no handhole shall be required in a pole that is 20 ft or less in height above grade, provided it has a hinged base. It’s obvious from the photo this pole does not have a hinged base.

Don't Buy Your Gas Here

“I took these photos at a gas station close to where I live,” says John Nuss, Mountaintop Electric, LLC, Fort Worth, Texas. “On a cloudy day, I pulled in and got out my static tester. Sure enough, these wires were hot! It has been like this for at least seven years. Needless to say, I don’t buy gas here, because it is too dangerous.”

As listed in 514.4 of the 2011 NEC, “All electrical equipment and wiring installed in Class I locations as classified in 514.3 shall comply with the applicable provisions of Art. 501.” An Exception to this requirement notes, “As permitted in 514.8.” An Informational Note in this section states: “For special requirements for conductor insulation, see 501.20.”

We can also make reference to 500.5(A), which states “Locations shall be classified depending on the properties of the flammable gas, flammable liquid-produced vapor, combustible-liquid produced vapors, combustible dusts, or fibers/flyings that may be present, and the likelihood that a flammable or combustible concentration or quantity is present. Where pyrophoric materials are the only materials used or handled, these locations shall not be classified. Each room, section, or area shall be considered individually in determining its classification.”

About the Author

Joe Tedesco

Tedesco served the industry in many roles during his career. He was a director, senior electrical code instructor for National Technology Transfer, Inc. and American Trainco, Inc.. He was also a codes, standards and seminar specialist for the International Association of Electrical Inspectors and an electrical field service specialist for the National Fire Protection Association in Quincy, Mass. He ran his own business as an NEC consultant and is a Massachusetts licensed master electrician and journeyman electrician and certified electrical inspector (one and two family 2A; General 2B, and Plan Review, 2C). Tedesco also wrote articles for CEE News and EC&M (Code Violations Illustrated and What's Wrong Here?) for more than 15 years and helped launched the Moving Violations video series.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.