All references are based on the 2017 edition of the NEC.
Elevator Room Escapades
The switch box in the foreground and the one in the background have a Code violation in common: Neither box is properly supported. The installer simply stuck an EMT connector onto the raceway coming up from the floor and used that as the support for the boxes. Section 358.12(1) prohibits using EMT for the support of luminaires or other equipment except for conduit bodies. A 4-in. square outlet box is not a conduit body and is not permitted to be supported by the EMT. Sections 314.23(E) and (F) both have provisions that allow certain raceways to support boxes, but the raceways must be RMC or IMC conduit threaded into the enclosure or hubs. The flexible metal conduit (FMC) connected to each box is also not permitted as a supporting means for outlet boxes or other enclosures. Another problem can be spotted on the box in the foreground. The bottom knockout seal is missing from the side of the box. You can see one of the circuit conductors through the opening. Section 110.12(A) requires unused openings to be closed in a manner that affords protection effectively equivalent to the wall of the enclosure.
Mulch Misery
Where is the missing cover? It may have helped prevent this buildup of mulch from wreaking havoc with this receptacle installation. Receptacles rated 15A or 20A, 125V or 250V installed in wet locations must have an enclosure that is weatherproof whether or not an attachment plug is plugged in. The missing cover results in this receptacle now being in an enclosure that is no longer weatherproof. It is certainly not mulch-proof either. Section 406.9(B)(1) also requires any outlet box hoods installed for this application to be listed and identified as “extra-duty.” Perhaps an “extra-duty” cover would have been durable enough to withstand the rigors of heavy usage. This cover apparently could not handle it, snapped off, and then went missing. For damp locations, Sec. 406.9(A) requires all nonlocking 15A and 20A, 125V- and 250V-rated receptacles to be listed as a weather-resistant type (WR). Section 406.9(B) has the same requirement for those types of receptacles when they are installed in wet locations too. We could also argue that this a violation of Sec. 110.12(B) because the missing cover adversely affects the safe operation and use of this equipment.
Russ LeBlanc