How well do you know the Code? Think you can spot violations the original installer either ignored or couldn't identify? Here's your chance to moonlight as an electrical inspector and second-guess someone else's work from the safety of your living room or office. Joe Tedesco, who has a knack for finding shoddy electrical work, did the dirty work and found this mess. Now it's your turn to identify the violation.

Find the Answer

Answer:

Tony Scaffidi, technical support engineer, Pieper Electric, Milwaukee, sent in these comments in reference to the March photograph. “This looks like a utility energy saving device that went wrong,” he wrote. He pointed out a violation of Art. 300, specifically 300.13(A) and (B), which states that conductors in raceways shall be continuous between boxes, devices, and similar components. He also noted that per 300.15, where the wiring method is conduit, as in the picture, a box or conduit body that complies with Art. 314 shall be installed at each conductor splice point, outlet point, junction point, pull point, or termination point unless otherwise permitted in 315(A) through (M).

Brian Newland, electrical designer, DWG, Inc., Savannah, Ga., identified four violations in his submission. “First, the conduit opening is not protected from the weather [110.12(A)],” he wrote. “Second, the conductors are most likely not rated for external use (310.13). Third, there is a possibility of electric shock from the conductors not having wire nuts [110.14(B)]. And fourth, there is an improper connection from conduit to box (300.18).”

Ivan Philipose, electrical engineer, Sidhu Associates, Inc., Hunt Valley, Md., noted three violations. “It seems power and low-voltage wiring are housed in the same raceway — this may not be allowed per 300.3(C),” he wrote. “Splices must be made in a junction box of adequate size to suit the fill requirements of 314.16, and be routed through a conduit nipple connected to the control box. And all unspliced wires must be taped and terminated in a waterproof junction box as per 110.14(B).”

> Try Another Quiz

About the Author

Joe Tedesco

Tedesco served the industry in many roles during his career. He was a director, senior electrical code instructor for National Technology Transfer, Inc. and American Trainco, Inc.. He was also a codes, standards and seminar specialist for the International Association of Electrical Inspectors and an electrical field service specialist for the National Fire Protection Association in Quincy, Mass. He ran his own business as an NEC consultant and is a Massachusetts licensed master electrician and journeyman electrician and certified electrical inspector (one and two family 2A; General 2B, and Plan Review, 2C). Tedesco also wrote articles for CEE News and EC&M (Code Violations Illustrated and What's Wrong Here?) for more than 15 years and helped launched the Moving Violations video series.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.