Hint: Check the length
The ground rod installed for this service creates several Code violations.
Section 250.53(G) of the 2014 NEC requires rod-type electrodes to be installed so that at least 8 ft of length is in contact with the soil. That would be impossible in this case because almost 3 ft of this rod is sticking up above grade. Even if this were a 10-ft rod, it would still be a violation because only 7 ft of it would be in contact with the soil.
In addition, the upper end of the rod is required to be “flush with or below ground level unless the rod and the electrode conductor attachment are protected against physical damage.” No protection was provided for this rod or conductor.
The clamp used to connect the wire to the rod appears to be a water pipe clamp instead of a clamp rated to be used on a ground rod. Section 250.70 requires ground clamps to be listed for use with the electrode material and also the conductor’s material. Where used on buried electrodes, the clamp must also be listed for direct burial or concrete encasement.
Finally, the rod sticking up from the ground also creates a violation of the clear working space requirements of Sec. 110.26(A)(1) through(3).
Russ LeBlanc