Hint: Peek-a-boo cable
The UF cable poking out of the ground is in serious danger of being damaged by a weed whacker or a lawn mower. In addition, it could easily be stepped on by anyone walking by it.
Section 340.12(10) of the 2014 NEC does not permit UF cable to be installed where it is subject to physical damage. This is also a violation of Sec. 300.5(D)(1), since cables and conductors emerging from the ground are required to be protected by enclosures or raceways from the minimum depth required by 300.5(A), to a point at least 8 ft above grade.
Starting the protection at 2 in. above grade does not really afford any protection to the cable. Where the raceway itself is subject to physical damage, Sec. 300.5(D)(4) requires RMC, IMC, RTRC-XW, Schedule 80 PVC, or some equivalent protection to be used. Sections 352.10(F) and 352.12(C) similarly require PVC to be identified for the use where installed in areas exposed to physical damage. Schedule 80 PVC is identified for use in areas exposed to physical damage. Using Schedule 40 PVC may not be the best option in this case because this is a high traffic area.
Russ LeBlanc