Can you identify the Code violation(s) in this photo?

How well do you know the Code? Think you can spot violations the original installer either ignored or couldn't identify? Here's your chance to moonlight as an electrical inspector and second-guess someone else's work from the safety of your living room or office. It's your turn to identify the violation.

Hint: Arranged to drain

March Winner

Our lone winner this month was Shauwn Collins, owner, Absolute Electric LLC, Sterling, Va. He properly noted that these receptacle outlet covers are not the “in use” type required by the NEC. The location in which they were installed is also a concern.

These receptacles supply power to some ice-melting cables installed in the gutter, downspouts, and on the roof of this building. The covers installed on these boxes are not the right type for the 125V, 15A receptacles being used at this outdoor wet location. According to the requirements in Sec. 406.9(B)(1), in this type of location the enclosure must be weatherproof whether or not the attachment plug is inserted. These covers are only weatherproof when they are closed. In addition, the receptacles themselves must be listed as weather-resistant type. According to Exception No. 2 of Sec. 210.8(B), these receptacles are not readily accessible and would not need GFCI protection. However, the listing instructions for these cord- and plug-connected electric ice melting cables generally require ground fault protection.

About the Author

Russ LeBlanc | Owner

Russ started in the electrical trade as an apprentice in 1985. He worked his way up to become a Journeyman Electrician and then eventually became a Master Electrician and Licensed Construction Supervisor. In 1999 Russ become an Electrical Instructor for The Peterson School of Engineering in Massachusetts where he developed his passion for teaching, and quickly became Department Head of Electrical Instruction. Russ has taught thousands of apprentices, electricians, engineers, inspectors, and other electrical professionals during his career as an instructor. He continues to provide electrical professionals with Electrical Code seminars, Arc-Flash Awareness training seminars and educational material through his LeBlanc Consulting Services in North Reading, MA whose specialty is educating electricians. He has been an active member of the NFPA Electrical Section and has authored hundreds of National Electrical Code proposals and comments which have become Code rules to improve the safety for the electrical industry. Russ is also an IAEI certified Electrical Inspector.

Please visit www.russleblanc.net for more information.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.