What’s Wrong Here? Hint: Creative Cable Connections
See answer below.
I’m not sure if this cable got yanked out of the connector after the installation, or if this was the way it was originally installed. In either case, there are a few Code violations we need to discuss.
Section 300.12 requires cable sheaths to be continuous between boxes, cabinets, fittings, enclosures or outlets. This cable sheath comes up a little short of the definition of “continuous.” Section 410.56(A) requires conductors for luminaires to be arranged in a way that will not cut or abrade the conductor insulation. Where passing through metal, Sec. 410.56(B) requires conductor insulation to be protected. The exposed conductors no longer comply with Sec. 310.10 since they are not inside the Chapter 3 wiring method of NM cable. Lastly, the NM cable connector is listed for use with NM cable, but not designed for use with individual conductors. Using the cable connector in this manner is a violation of Sec. 110.3(B).
Russ LeBlancRuss LeBlanc