What’s Wrong Here? Hint: Foot Lug Failure
Dec. 3, 2020
Hint: Foot lug failure.
I noticed some problems when I removed the cover from this enclosure. If you look closely at the foot lugs installed inside the bottom right of this panelboard enclosure you can see multiple equipment grounding conductors (EGCs) shoved into each lug. Installing multiple wires in a terminal designed for only one conductor is a violation of Sec. 110.3(B). Section 110.14(A) requires terminals designed for more than one conductor to be identified for this purpose. Where separate EGCs are provided, Sec. 408.40 requires a terminal bar to be secured inside the panelboard cabinet, with the terminal bar bonded to the metal cabinet. There is no terminal bar installed for terminating the EGCs in this enclosure.
Russ LeBlanc
Russ LeBlanc