Electrical Troubleshooting Quiz — Dec. 3, 2019
An 800A molded-case circuit breaker that feeds a critical area of the plant started having nuisance trips. The first few times, maintenance would look for obvious problems and perform testing to verify no circuits were faulted to ground. Then, they would reset the breaker. After a while, they stopped performing testing and would just reset the breaker.
This is the plant electrical engineer's first job since graduating, and his education had not prepared him for what to do in this case. The senior electrician said there was a spare breaker in the stockroom, so they should just replace the one that is nuisance tripping.
That's what they did, but the problem persisted. What should they do now?
That's an expensive item to simply replace. And what is the condition of the one that was in the stockroom? Was that spare regularly maintained? At least lubricated and tested? Or was it simply assumed to be in serviceable condition? It's possible both breakers are bad.
It's also possible that something real is causing the breaker to trip. Get a thermographic image of the breaker now in service, perhaps multiple times. Next, connect a power analyzer so you can see what's going on both upstream and downstream of that unit. Leave it connected long enough to capture the next nuisance trip.
Contact a qualified electrical testing firm to test the original breaker. If they deem the breaker serviceable, have them perform the factory required maintenance on that breaker. Now you have a known good breaker. Schedule downtime to install it.
Mark LamendolaMark Lamendola
Related
Quiz Graphic
green quiz dice stuartmiles99 iStock Getty Images Plus
