Electrical Troubleshooting Quiz — June 3, 2019

The first rule of breaker testing is never operate the breaker before testing it.
June 4, 2019
2 min read

You’ve been called in to consult on a problem that has plagued the 480V circuit breakers for quite some time. Three electricians have worked on them, and all three say the breakers behave erratically. They have similar accounts of the behavior.

One 400A breaker, for example, was showing 402A during a routine PM in which one step was to measure the current using an inductive clamp. Some sources of overload were identified and corrected for, dropping the current to 350A. During a planned shutdown, that electrician was able to manually operate the breaker. He then used a breaker tester and found the breaker tripped exactly as it was supposed to.

What’s going on?

The first rule of breaker testing is never operate the breaker before testing it. The reason is you must also test the lubricant. Grease hardens over time because of oxidation and other factors; in that condition it will impede the movement of parts. Manually operating the breaker cracks the hardened film of the grease but doesn’t restore the lubricant to its required properties.

It isn’t that the breakers are behaving erratically. They are being tested improperly and they aren’t being maintained. The examples are similar, and the one example clearly indicates a sticking mechanism.

The solution is to schedule every 480V breaker for a complete PM, including a lubrication change. Have this done by a qualified electrical testing firm; the in-house electricians lack the skills and would also lack the time during the shutdown window.

About the Author

Mark Lamendola

Mark Lamendola

Mark is an expert in maintenance management, having racked up an impressive track record during his time working in the field. He also has extensive knowledge of, and practical expertise with, the National Electrical Code (NEC). Through his consulting business, he provides articles and training materials on electrical topics, specializing in making difficult subjects easy to understand and focusing on the practical aspects of electrical work.

Prior to starting his own business, Mark served as the Technical Editor on EC&M for six years, worked three years in nuclear maintenance, six years as a contract project engineer/project manager, three years as a systems engineer, and three years in plant maintenance management.

Mark earned an AAS degree from Rock Valley College, a BSEET from Columbia Pacific University, and an MBA from Lake Erie College. He’s also completed several related certifications over the years and even was formerly licensed as a Master Electrician. He is a Senior Member of the IEEE and past Chairman of the Kansas City Chapters of both the IEEE and the IEEE Computer Society. Mark also served as the program director for, a board member of, and webmaster of, the Midwest Chapter of the 7x24 Exchange. He has also held memberships with the following organizations: NETA, NFPA, International Association of Webmasters, and Institute of Certified Professional Managers.

Sign up for our eNewsletters
Get the latest news and updates

Voice Your Opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!