Article 680, Part V provides the requirements for permanently installed fountains. Some highlights include:
- Any submersible equipment used with a fountain must be GFCI-protected [680.51(A)]. But this requirement does not apply to submersible equipment that is listed for operation at low voltage contact (or less) and supplied by a power source that complies with 680.23(A)(2).
- Luminaires for fountain basins are typically designed to be water cooled, so the lens must be below the normal water level unless listed for above-water locations [680.51(C)].
- Luminaires aren't the only kinds of equipment that rely on submersion for safe operation. Protect all such equipment from overheating via a low-water cut-off or other approved means [680.51(D)].
- All metal piping systems associated with the fountain must be bonded to the equipment grounding conductor (EGC) of the branch circuit supplying the fountain [680.53]. Bonding equipment to a ground rod (instead) will create a shock hazard.
- You will find “grounding” requirements in 680.54 and 680.55. Be careful here. What is meant by “ground” is a connection to the EGC (a low impedance path to the source).