Q. What are the field marking requirements for available fault current at electrical service equipment?

A. Service equipment in other than dwelling units must be legibly field-marked with the maximum available fault current, including the date the fault current calculation was performed, and be of sufficient durability to withstand the environment involved [110.24(A)], as shown in the Figure. When modifications to the electrical installation affect the maximum available fault current at the service, the maximum available fault current must be recalculated to ensure the service equipment ratings are sufficient for the maximum available fault current at the line terminals of the equipment. The required field marking(s) in 110.24(A) must be adjusted to reflect the new level of maximum available fault current [110.24(B)].

Exception: Field markings aren’t required for industrial installations where conditions of maintenance and supervision ensure that only qualified persons service the equipment.

Q. Are flexible metal conduit and liquidtight flexible metal conduit allowed to serve as equipment grounding conductors per the NEC?

A. In order for flexible metal conduit or liquidtight flexible metal conduit to serve as an equipment grounding conductor, the following conditions must be met [250.118]:

Listed flexible metal conduit (FMC):

  1. The raceway terminates in listed fittings.
  2. The circuit conductors are protected by an overcurrent device rated 20A or less.
  3. The combined length of the flexible conduit in the same ground-fault current path doesn’t exceed 6 ft.
  4. If flexibility is required to minimize the transmission of vibration from equipment or to provide flexibility for equipment that requires movement after installation, an equipment grounding conductor of the wire type must be installed with the circuit conductors in accordance with 250.102(E), and it must be sized according to 250.122, based on the rating of the circuit overcurrent device.

Listed liquidtight flexible metal conduit (LFMC) where:

  1. The raceway terminates in listed fittings.
  2. For 3/8 in. through ½ in., the circuit conductors are protected by an overcurrent device rated 20A or less.
  3. For ¾ in. through 1¼ in., the circuit conductors are protected by an overcurrent device rated 60A or less.
  4. The combined length of the flexible conduit in the same ground-fault current path doesn’t exceed 6 ft.
  5. If flexibility is required to minimize the transmission of vibration from equipment or to provide flexibility for equipment that requires movement after installation, an equipment grounding conductor of the wire type must be installed with the circuit conductors in accordance with 250.102(E), and it must be sized in accordance with 250.122, based on the rating of the circuit overcurrent device.

Q. Are there any AFCI requirements for circuit modifications or additions to existing circuits?

A. Yes, according to 210.12(B), where the branch circuit wiring in a dwelling unit is modified, replaced, or extended in any of the areas specified in 210.12(A), the branch circuit must be protected by:

  1. A listed combination AFCI located at the origin of the branch circuit; or
  2. A listed outlet branch circuit AFCI located at the first receptacle outlet of the existing branch circuit.
About the Author

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.