Q. When multiple branch circuits are present in an enclosure, what does the Code require in regard to grouping of neutral conductors?
A. The ungrounded and neutral conductors of multiple branch circuits must be grouped together by cable ties or similar means in every enclosure [200.4(B)], as shown in the Figure.
Exception No. 1: Grouping isn’t required where the circuit conductors are contained in a single raceway or cable unique to that circuit that makes the grouping obvious.
Exception No. 2: Grouping isn’t required if the conductors pass through a box or conduit body without any splices or terminations, or if the conductors don’t have a loop as described in 314.16(B)(1).
Section 210.4(D) contains a similar requirement for branch circuit conductors.
Mike HoltMike Holt