Q. How do you determine the minimum number of general lighting and general-use branch circuits required by the NEC for dwellings?
A. The minimum number of general lighting and general-use receptacle branch circuits must be determined by dividing the total calculated load in amperes by the ampere rating of the circuits used [210.11(A)].
For example, let’s say you’re trying to determine how many 15A, 120V circuits are required for the general lighting and general-use receptacles for a dwelling having floor area of 1,500 sq ft, exclusive of an unfinished cellar not adaptable for future use [Example D1(a) in Annex D]?
Step 1: Determine the total VA load.
VA = 1,500 sq ft x 3VA per sq ft [Table 220.12]
VA = 4,500VA
Step 2: Now solve for the amperes.
I = VA ÷ E
I = 4,500VA ÷ 120V
I = 38A
Step 3: Determine the number of circuits.
Number of Circuits = 38A ÷ 15A
Number of Circuits = Three 15A or two 20A
Note: There’s no limit to the number of receptacles on a circuit in a dwelling unit.
If you calculate the load based on the volt-amperes/square foot method, the wiring system must be provided to serve the calculated load, with the loads evenly proportioned among multioutlet branch circuits within the panelboard.
These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code