Q. What is the Code rule regarding support of raceways and boxes by a cable tray?

See the answer below.

A. In industrial facilities where conditions of maintenance and supervision ensure only qualified persons will service the installation, and if the cable tray system is designed and installed to support the load, cable tray systems can support raceways, cables, boxes, and conduit bodies [392.18(G)] (Figure). 

For raceways terminating at the tray, a listed cable tray clamp or adapter must be used to securely fasten the raceway to the cable tray system. The raceway must be supported in accordance with the appropriate raceway Article.

Raceways or cables running parallel to the cable tray system can be attached to the bottom or side of a cable tray system. The raceway or cable must be fastened and supported in accordance with the appropriate raceway or cable’s Code Article.

Boxes and conduit bodies attached to the bottom or side of a cable tray system must be fastened and supported in accordance with Sec. 314.23.

These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code. 

About the Author

Mike Holt

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.