Code Q&A: Sizing OCPDs for Appliance Branch Circuits
See if you can answer this Code question.
Q. What are the NEC branch circuit overcurrent protection requirements for appliance circuits?
See the answer below.
A. As per Sec. 422.11(A), branch-circuit conductors must have overcurrent protection in accordance with Sec. 240.4, and the overcurrent protection device rating must not exceed the rating marked on the appliance.
For non-motor appliances, the appliance overcurrent protection device must:
(1) Not exceed the rating marked on the appliance.
(2) Not exceed 20A if the overcurrent protection device rating isn’t marked, and the appliance is rated 13.30A or less, or
(3) Not exceed 150% of the appliance rated current if the overcurrent protection device rating isn’t marked, and the appliance is rated over 13.30A. Where 150% of the appliance rating doesn’t correspond to a standard overcurrent protection device ampere rating listed in Sec. 240.6(A), the next higher standard rating is permitted.
Mike Holt
Mike Holt