Q. What is the Code required method of sizing the conductors to a single continuous-duty motor?

See answer below. 

A. Conductors to a single motor must be sized not less than 125% of the motor FLC rating as listed in Table 430.247 [Direct-Current Motors], Table 430.248 [Single-Phase Motors], or Table 430.250 [Three-Phase Motors] [Sec. 430.22].

Example: What size circuit conductor is required for a 3 hp, 230V, single-phase motor?

Solution: Determine the branch-circuit conductor size based on the motor’s FLC [Sec. 430.6(A)(1), Sec. 430.22(A) and Table 310.15(B)(16)].

3 hp, 230V Motor FLC = 17A [Table 430.248]

17A × 1.25 = 21.25A

Answer: 10 AWG rated 30A at 60°C [Table 310.15(B)(16)]

The branch-circuit circuit breaker overcurrent protection is based on motor’s FLC [240.6(A), 430.6(A)(1), 430.52(C)(1), and Table 430.248].

The circuit equipment grounding conductor must be sized to the 45A overcurrent protection device — 8 AWG [Table 250.122], but it’s not required to be sized larger than the circuit conductors — 10 AWG.

Example: What size branch-circuit conductor and overcurrent protection device is required for a 7½ hp, 230V, three-phase motor with 60ºC terminals?

Solution: Motor FLC = 22A [Table 430.250]

Conductor Size = 22A × 1.25 = 27.50A

Note: The branch-circuit short-circuit and ground-fault protection device using an inverse time breaker is sized at 60A in accordance with Sec. 430.52(C)(1), Exception No. 1.

Circuit Overcurrent Protection = 22A × 2.50 = 55A

Answer: A 10 AWG conductor rated 30A at 60°C [Sec. 110.14(C)(1), Table 310.15(B)(16)] and a 60A (next size up from 55A) overcurrent protection device [Sec. 240.6(A)].

These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code. 

About the Author

Mike Holt

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Sign up for our eNewsletters
Get the latest news and updates

Voice Your Opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!