Code Quiz: Sizing Conductors for a Single Motor Load
Based on the 2020 NEC.
Question: What is the minimum ampacity for a conductor supplying a 480V, 10 HP motor with a nameplate current of 13A?
See answer below.
Answer: 17.5A
Explanation: Section 430.6(A)(1) of the 2020 NEC requires the current value for sizing conductors to be based on Table 430.250. For the motor listed above, the value would be 14A. Section 430.22 requires this value to be multiplied by 125% (14 X 125% = 17.5A).
Lupacchino is a senior design engineer with Gaylor Electric, Inc. in Noblesville, Ind. and serves as an alternate on NEC Code-Making Panel No. 3. He is currently licensed in more than 80 jurisdictions. He can be reached at [email protected].