A branch circuit overcurrent device is a device capable of providing protection...
Fill in the blank
A branch circuit overcurrent device is a device capable of providing protection for ________, _________, and branch circuits and equipment over the full range of overcurrents between its rated current and its interrupting rating. Branch circuit overcurrent protective devices are provided with interrupting ratings appropriate for the intended use, but no less than 5,000A.
  1. overloads, underloads
  2. service, feeder
  3. taps, conductors
  4. auxiliary gutters, wireways
Answer: B
The definition of a branch circuit overcurrent device is outlined in Art. 100 as follows: "A branch circuit overcurrent device is a device capable of providing protection for service, feeder, and branch circuits and equipment over the full range of overcurrents between its rated current and its interrupting rating. Branch circuit overcurrent protective devices are provided with interrupting ratings appropriate for the intended use, but no less than 5,000A."