When installing a THHN / THWN insulated conductor in a raceway that is located on the outside wall of a building or structure (wet location), the choice for the type of conductor insulation is permitted to be based on _____________.
A. the use of THHN insulation rating, based on a dry location rating, as the inside of the raceway is considered to be a dry location. The installation shall also comply with 310.10(C).
B. the use of THWN insulation rating, based on a wet location rating, as the inside of the raceway is considered to be a wet location. The installation shall also comply with 310.10(C).
C. all of the applicable rules for a rooftop installation.
D. the application adjustment factors for conductors installed in raceways located on the outside wall.
Answer: B
As outlined in Sec. 300.9 of the NEC, “Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location.” A similar change was made in 300.38 in the 2014 NEC for installations above 1,000V nominal.