Horrible Hotel Wiring

Gregg Sutton with TPC Training in West Virginia was kind enough to share this great photo with us.

“I found this in my room while teaching an electrical troubleshooting class at a well-known hotel chain in Mobile, Ala.,” said Sutton. “I noticed exposed wire nuts under the HVAC unit and investigated. This mess was shoved underneath, and I pulled it out (as shown in the picture). When I asked my students who were staying at the hotel to check their rooms, they found similar results. I showed the hotel manager, and I tried to get across how dangerous it was.”

I think many of our readers would also agree that this presents a dangerous situation. Section 300.15 requires a box or conduit body to be installed wherever conductor splices are made or outlets such as receptacles are installed when the wiring methods are flexible metal conduit (FMC), type MC cables, and other raceways or cable wiring methods.

Section 400.13 requires flexible cords to be installed in continuous lengths having no splices. Repairing hard-service cord and junior hard-service cord is permitted. This air conditioner most likely uses an SP-3 type power supply cord. The lack of continuity between the metal conduits and the equipment grounding conductors violates Sec. 300.10.

Car Dealership Debacle

Scott Chisholm, an electrical instructor and wire inspector from Needham, Mass., found this mess while inspecting a building at a local car dealership. All the debris being stored in the working space in front of these panelboards violates Sec. 110.26(B). Working space must be kept clear and cannot be used for storage. All this stored junk also hinders access to the overcurrent devices and is a violation of Sec. 240.24(A), as the circuit breakers are presently not readily accessible as required.

Storing easily ignitable or flammable material near these overcurrent devices violates Sec. 240.24(D). What might be the worst of all is that someone mistakenly thought storing gasoline here was a good idea.

In addition, the covers missing from the meter socket enclosure and panelboard increase the chances of a person making accidental contact with exposed energized parts and receiving a shock. This is a violation of Sec. 110.27(A). The metal wireway without a cover is a violation of Sec. 376.100(D). Using duct tape to cover the openings where circuit breakers would normally be installed is a violation of Sec. 408.7.

About the Author

Russ LeBlanc

Russ LeBlanc

Owner

Russ started in the electrical trade as an apprentice in 1985. He worked his way up to become a Journeyman Electrician and then eventually became a Master Electrician and Licensed Construction Supervisor. In 1999 Russ become an Electrical Instructor for The Peterson School of Engineering in Massachusetts where he developed his passion for teaching, and quickly became Department Head of Electrical Instruction. Russ has taught thousands of apprentices, electricians, engineers, inspectors, and other electrical professionals during his career as an instructor. He continues to provide electrical professionals with Electrical Code seminars, Arc-Flash Awareness training seminars and educational material through his LeBlanc Consulting Services in North Reading, MA whose specialty is educating electricians. He has been an active member of the NFPA Electrical Section and has authored hundreds of National Electrical Code proposals and comments which have become Code rules to improve the safety for the electrical industry. Russ is also an IAEI certified Electrical Inspector.

Please visit www.russleblanc.net for more information.

Sign up for our eNewsletters
Get the latest news and updates

Voice Your Opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!