What's Wrong Here? Hint: It’s as Plain as Black and White.
NEC Consultant Russ LeBlanc stumbled across this installation. Think you know how it violates the NEC? Hint: Round and round she goes. Hint: It’s as plain as black and white.
How well do you know the Code? Think you can spot violations the original installer either ignored or couldn’t identify? Here’s your chance to moonlight as an electrical inspector and second-guess someone else’s work from the safety of your living room or office. Can you identify the specific Code violation(s) in this photo? Note: Submitted comments must include specific references from the 2020 NEC.
December Winner
Our lone winner this month was Jacob Jeffcoat, a journeyman electrician with IBEW 1141 from Oklahoma City. He knew there were lots of violations to discuss here.
The first problem is the equipment grounding conductor (EGC) wrapped around the yellow NM cable with no connection to the other equipment grounds installed in the box. Section 250.148(C) requires all EGCs to have a connection to the metal box in accordance with Sec. 250.8.
The next problem is the missing knockout on the left side of the box. This violates Sec. 110.12(A). Unused openings must be closed to afford protection similar to the wall of the box. A closer look at the cable clamp used to secure the two cables entering the bottom of the box reveals a violation of Sec. 300.15. Fittings and connectors must be used only with the wiring methods for which they are specifically designed and listed. This cable clamp is designed and listed for metal cables such as MC and AC cables.
Lastly, the lack of any box cover is a violation of Sec. 314.25, which requires each box to have a cover, faceplate, lampholder, or canopy for a completed installation.
Russ LeBlanc
Russ LeBlanc