Sizing a Supply-Side Bonding Jumper
Part V of Article 250 focuses on bonding requirements.
What is the minimum size supply-side bonding jumper for a service raceway containing 4/0 THHN aluminum conductors?
a) 6 AWG aluminum
b) 4 AWG aluminum
c) 4 AWG copper
d) 3 AWG copper
The correct answer is: c) 4 AWG copper
Article 250 covers the general requirements  for grounding and bonding electrical installations. Part V of this Article focuses on bonding requirements. More specifically, supply-side bonding jumper sizing requirements can be found in Sec. 250.102(C).
As noted in 250.102(C)(1), "The supply-side bonding jumper shall not be smaller than specified in Table 250.102(C)(1)." A quick check of this Table reveals you must use a 4 AWG copper bonding jumper in this situation.
Mike Holt
Mike Holt