The Basics of Arc-Fault Protection

Although new to the NEC, AFCIs are important for protecting against arc faults. Unsafe arc faults can occur as series or parallel arcs. A series arc can occur when the conductor in series with the load breaks. The series configuration means the arc current cannot be greater than the load current the conductor serves. Typically, series arcs don't develop sufficient thermal energy to create a fire.

Although new to the NEC, AFCIs are important for protecting against arc faults.

Unsafe arc faults can occur as series or parallel arcs. A series arc can occur when the conductor in series with the load breaks. The series configuration means the arc current cannot be greater than the load current the conductor serves. Typically, series arcs don't develop sufficient thermal energy to create a fire.

More dangerous is the parallel arc fault, which can occur as a short circuit or a ground fault. A short circuit arc decreases the dielectric strength of insulation separating the conductors, allowing a high-impedance, low-current arc fault to develop that carbonizes the conductor's insulation, further decreasing the dielectric of the insulation separating the conductors. The result is increased current, exponentially increased thermal energy, and the likelihood of a fire. The current flow in a short circuit, parallel arc fault is limited by the system impedance and the impedance of the arc fault itself.

A ground fault parallel arc fault can occur only when a ground path is present. This type of arc fault can be cleared by a GFCI or an AFCI. The RMS current value for parallel arc faults will be considerably less than that of a solid, bolted-type fault. Therefore, a typical 15A breaker might not clear this fault before a fire ignites.

UL 1699 contains the requirements for listing AFCI devices. Each type of AFCI protects different aspects of the branch circuit and extension wiring. However, only the branch/feeder AFCI meets NEC requirements. AFCIs are not designed to prevent fires caused by series arcing at loose connections. Let's look at examples of AFCIs.

Branch/feeder AFCI.

This device is installed at the origin of a branch circuit or feeder like a panelboard. It provides parallel arc-fault protection for branch circuit wiring, cord sets, and power supply cords. It's not UL-Listed to provide series-type arc-fault protection.

Combination AFCI.

This device, which is typically a receptacle, provides parallel and series arc-fault protection for branch circuit wiring, cord sets and power supply cords downstream from the device. It doesn't, however, provide parallel arc-fault protection upstream.

Outlet circuit AFCI

This device is installed at a branch circuit outlet. It provides parallel and series arc-fault protection for the cord sets and power-supply cords plugged into the outlet. However, it doesn't provide arc-fault protection on feed-through branch circuit conductors, nor does it provide parallel arc-fault protection upstream from the device.

Although AFCIs have their uses, it's important to note that these protection devices are not designed to prevent fires caused by series arcing at loose connections in devices like switches or receptacles.

About the Author

Mike Holt

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Sign up for our eNewsletters
Get the latest news and updates

Related

Courtesy of American Circuit Breaker Manufacturers Association
Curated Item 2

Voice Your Opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!