Electrical Troubleshooting Quiz — Nov. 6, 2018
The plant has been experiencing nuisance tripping of circuit breakers. Sometimes it’s a feeder breaker, sometimes it’s a branch circuit breaker. The procedure for addressing these trips is:
- Use a DMM to check the load side terminals for a short in the connected load.
- Disconnect all loads, and visually inspect each one.
- Where practical, perform insulation resistance testing on the circuit conductors.
- If no problems are found, close the breaker. Reconnect each load one at a time.
- Perform voltage and current checks with loads connected.
Only rarely have any problems been found. Adding to the frustration, the nuisance trips repeat in the same areas of the plant even though the breaker trip reset procedure has been repeatedly performed. How can you solve this?
You don’t want your feeder breakers serving as “backup protection” for any of your branch circuit breakers. It sounds like this is one thing that’s going on, so a coordination study is needed. Also, a determination of the correct breaker for a given circuit must be made (based on load characteristics) along with a determination of the settings for each breaker.
The trip response procedure is better than what’s typical, but a DMM operates on 9V and your feeders operate at 480V. There may be system defects that neither the DMM nor the insulation resistance tester can identify. Consult with a qualified testing firm.
Mark LamendolaMark Lamendola
Related
quiz computer keyboard