Code Quiz
What is the minimum acceptable voltage at a fire pump motor’s terminals, when the 460V-rated motor is supplied with an operating voltage of 480V, and the motor is operating at 115% of the full-load current rating of the motor?
Q. What is the minimum acceptable voltage at a fire pump motor’s terminals, when the 460V-rated motor is supplied with an operating voltage of 480V, and the motor is operating at 115% of the full-load current rating of the motor?
A) 465.6V
B) 445.6V
C) 437V
D) 408V
Answer: C
Explanation: As per 695.7 of the 2005 NEC, the maximum voltage drop permitted when the motor is operating at 115% of the full-load current rating of the motor is 5%. Since the voltage rating of the motor is 460V, the calculation is as follows: 460V x .05 = 23V. Therefore, the minimum voltage permitted at the motor terminals is: 460V – 23V = 437V.