NEC General Requirements for Branch Circuits, Part 2
Article 210 provides the requirements for branch circuits. As with most NEC articles, it has its own general requirements. Like the arrangement in many articles, those consist of Part I. Section 210.5 provides requirements for the identification of branch circuits.
It starts off with A, B, C: grounded conductor, equipment grounding conductor, and ungrounded conductors. It makes short work of the first two:
- Identify the grounded conductor per Sec. 210.7 [Sec. 210.5(A)].
- Identify the equipment grounding conductor per Sec. 250.119 [Sec. 210.5(B)].
Not so short when it comes to the identification requirements of ungrounded conductors. It considers three types:
- Branch circuits supplied from one nominal voltage system.
- Branch circuits supplied from more than one nominal voltage system.
- Branch circuits supplied from DC systems.
Let’s look at each of these in order.
Branch circuits supplied from one nominal voltage system must be identified per Sec. 310.6(A)(3) [Sec. 210.5(C)(1)]. That has a lot of text that boils down into “make it clear they are not grounded or grounding conductors.”
If you have more than one nominal voltage system, that rule also applies. In addition, you have to identify each ungrounded conductor of a branch circuit by phase (or line) and nominal voltage at each termination, connection, and splice. You also have to document the method in a manner that is readily accessible or permanently post this information at each branch-circuit panelboard or similar branch-circuit distribution equipment. The exception to this rule is when you have an existing voltage system and then add a new one; you need to mark only the new one. By default, the other one is marked by not being marked but you still have to include these words on the new system label: “Other unidentified systems exist on the premises” [Sec. 210.5(C)(2)].
If you have branch circuits supplied by DC system operating at more than 60V, you have to mark each ungrounded conductor that is 4 AWG or larger with its polarity at each termination, connection, and splice [Sec. 210.5(C)(3)]. For ungrounded conductors that are 6 AWG or smaller, you have to use one of the identification means listed in Sec. 210.5(C)(3)(a) for the positive (for example, a continuous red outer finish) and one of the identification means listed in Sec. 210.5(C)(3)(b) for the negative (for example, a continuous black outer finish).