Make Your Next Optical Fiber Installation Shine
Make Your Next Optical Fiber Installation Shine
The Code requirements for optical fiber vary with the type of cable used
Fiber optic cable has many advantages over competing technologies, including increased information capacity (by orders of magnitude), reduced ancillary equipment requirements in key applications, immense scalability and expandability with the same infrastructure, and electromagnetic noise immunity. For these reasons and others, fiber-optic cable installations are becoming increasingly common.
Art. 770 covers the installation of optical fiber cables used to transmit light for control, signaling, and communications. Further, it contains the installation requirements for optical raceways, which contain and support the optical fiber cables. It also contains the requirements for composite cables, often called “hybrids,” which combine optical fibers with current-carrying metallic conductors.
When you think of wiring methods, you probably think of Art. 300. However, you only need to use Art. 770 methods for fiber optic cables, except where Art. 770 makes specific references to Art. 300. The first such reference is to 300.21, which addresses requirements for stopping the spread of combustion. Openings around electrical penetrations through fire-resistant rated walls, partitions, floors, or ceilings must be firestopped using approved methods to maintain the fire resistance rating (770.3). You must also remove the accessible parts of abandoned fiber optic cables.
Art. 770 doesn't refer to 300.15, so you don't have to use boxes for splices or termination of optical fiber cable. The FPN in 770.50 states that splice cases and terminal boxes are typically used as enclosures for splicing or terminating optical fiber cables. But an FPN isn't an enforceable code requirement [90.5(C)]. On the other hand, composite optical fiber cables [770.5(C)] must comply with the appropriate requirements of Chapters 1 through 4 of the NEC.
Another Chapter 3 reference addresses ducts, plenums, and other air-handling spaces. You must follow 300.22 when installing optical fiber cables and optical fiber raceways in such spaces.
Optical fiber cables.
Optical fiber cables transmit light for control, signaling, and communications through an optical fiber. The NEC recognizes three types:
Nonconductive (Fig. 1 above). These fibers contain nothing that can conduct electricity, so they won't accidentally energize or be energized even when closely associated with electrical conductors.
Conductive. These fibers contain noncurrent-carrying conductive members, such as metallic strength members, metallic vapor barriers, and metallic armor or sheath.
Composite. These fibers contain optical fibers and current-carrying electrical conductors. Classify these as electrical cables in accordance with the type of electrical conductors. [770.52(A)]. Use composite cables only where the optical fibers and current-carrying electrical conductors are functionally associated.
You must meet Chapter 3 raceway requirements, but there are exceptions. For example, when your raceway contains only nonconductive cables, you can ignore the Chapter 3 and Chapter 9 wire fill requirements. Otherwise, those requirements apply (Fig. 2).
In an optical raceway, you can use only nonconductive optical fiber cables. This is a manufacturer's listing requirement and not found in the NEC. Instead, see the UL General Information for Electrical Equipment Directory.
It's also important to remember that you must route those cables so they don't prevent the removal of suspended ceiling panels. That goes hand in hand with 770.8, which requires you to install equipment and cabling in a neat and workmanlike manner. One aspect of that pertains to cables exposed on the surface of ceilings and sidewalls. You must support these by the structural components of the building in such a manner that normal use won't damage the cable. You must secure a cable in a manner that doesn't damage it. If you install cables next to framing members, you must protect them from physical damage via penetration by screws or nails. This requires a 1.25-in. separation from the framing member or a suitable metal plate per 300.4(D).
Listing and marking.
Indoors, you must use optical fiber cables that are listed as suitable for the application, and they must be marked per the requirements of Table 770.50. However, there is one exception. You don't need to use listed cables if the length of the cable within the building — measured from its point of entrance — doesn't exceed 50 ft and the cable terminates in an enclosure.
Here's a quick summary of the listing requirements for optical fiber cables and raceways, as laid out in 770.51:
Types OFNP and OFCP (Plenum). Suitable for use in ducts, plenums, and other space used for environmental air.
Types OFNR and OFCR (Riser). Suitable for use in a vertical run in a shaft or from floor to floor.
Types OFNG and OFCG (General-purpose). Suitable for general-purpose use, with the exception of risers and plenums.
Types OFN and OFC (General-purpose). Suitable for general-purpose use, with the exception of risers, plenums, and other space used for environmental air.
Plenum optical fiber raceway. Feature adequate fire-resistant and low smoke-producing characteristics (Fig. 3).
Riser optical fiber raceway. Feature fire-resistant characteristics capable of preventing the spread of fire from floor to floor.
General-purpose optical fiber cable raceway. Resistant to the spread of fire.
Mixing fiber and power cables.
If you're mixing optical fiber with other kinds of cabling, pay close attention to 770.52. The requirements can get tricky, but here are the highlights.
You can put optical fibers within the same composite cable for electric light, power, and Class 1 circuits that operate at 600V or less where the functions of the optical fibers and the electrical conductors are associated. This part of 770.52(A) gives permission for a factory-made composite optical fiber cable (hybrid cable). These composite cables have both optical fibers and current-carrying electrical conductors [770.5(C)]. You can use this type of optical fiber cable only where the optical fibers are functionally associated with the electrical conductors.
Nonconductive optical fiber cables, but not conductive optical fiber cables, can occupy the same cable tray or raceway as conductors for electric light, power, and Class 1 circuits operating at 600V or less.
Composite optical fiber cables containing only current-carrying conductors for electric light, power, and Class 1 circuits rated 600V or less can occupy the same cabinet, cable tray, outlet box, panel, raceway or other termination enclosure as conductors for electric light, power, and Class 1 circuits operating at 600V or less.
Nonconductive optical fiber cables can't occupy the same cabinet, outlet box, panel, or similar enclosure housing the electrical terminations of an electric light, power, and Class 1 circuit, with the following exceptions:
-
Exception No. 1. They can occupy the same cabinet, outlet box, panel, or similar enclosure where nonconductive optical fiber cable is functionally associated with the electric light, power, and circuit.
-
Exception No. 2. They can occupy the same cabinet, outlet box, panel, or similar enclosure where nonconductive optical fiber cables are installed in factory- or field-assembled control centers.
-
Exception No. 3. In industrial establishments only, where conditions of maintenance and supervision ensure that only qualified persons will service the installation, you can run nonconductive optical fiber cables with circuits exceeding 600V.
-
Exception No. 4. This is the same as No. 3, but for composite cables.
Optical fibers can be in the same cable — and conductive and nonconductive optical fiber cables can be in the same cable tray or enclosure — as any of the following (Fig. 4):
-
Class 2 and Class 3 circuits in compliance with Art. 725.
-
Power-limited fire alarm circuits in compliance with Art. 760.
-
Communications circuits in compliance with Art. 800.
-
CATV cables in compliance with Art. 820.
Applications.
In 770.53, the various requirements for plenums and risers can seem like alphabet soup. Even so, you'll need to match the cable type to the application. Figure 770.53 can help. You must also consider the type of raceway you're using, whether there are floor penetrations, and whether the installation is in a single-family home, duplex, or other type of building.
Perhaps the most important concept to remember about Art. 770 is something it doesn't even cover: Art. 90's statement that the NEC isn't a design guide or installation manual. Art. 770 doesn't tell you how to ensure your system will meet, and test out to, the necessary performance requirements or contract specifications. It makes no mention of maximum bend radii and doesn't tell you how to install and test cable safely — for example, it doesn't caution you to not to look into a cable even if you can't see any light coming through it. The light might not be visible, but it can still damage your eye. Use Art. 770 in concert with other standards, and your fiber optic work will shine.
About the Author
Mike HoltMike Holt
Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.