Code Q&A: Appliance Disconnecting Means

Test your NEC knowledge.

Q. What are the NEC rules for the disconnecting means of appliances?

See the answer below.

Underline text indicates a 2020 Code change.

A. Each appliance must have a means that disconnects simultaneously all ungrounded circuit conductors [Sec. 422.30].

Permanently Connected Appliance Disconnects [Sec. 422.31]

(A) Appliances Rated at Not Over 300VA or 1/8 Horsepower. For 300VA or 1/8 horsepower or less appliances, a circuit breaker located within sight from the appliance, or is lockable with provisions for locking to remain in place whether the lock is installed or not in accordance with Sec. 110.25, can serve as the disconnect means.

(B) Appliances Rated Over 300VA. For appliances rated over 300VA, a switch or circuit breaker located within sight of the appliance, or is lockable with provisions for locking to remain in place whether the lock is installed or not in accordance with Sec. 110.25, can serve as the disconnect means. (Figure)

According to Art. 100, “Within Sight” means that it’s visible and not more than 50 ft from one to the other.

(C) Motor‑Operated Appliances Rated Over 1/8 Horsepower. For motor‑operated appliances rated over 1/8 horsepower, the disconnect must be located within sight from the motor‑operated appliance or be lockable with provisions for locking to remain in place whether the lock is installed or not in accordance with Sec. 110.25.

Exception: An appliance containing a unit switch that complies with Sec. 422.34.

Cord-and-Plug-Connected or Attachment Fitting–Connected Disconnects

(A) Attachment Plug and Attachment Fitting. Cord‑and‑plug or attachment fitting‑connected appliances can serve as the disconnecting means [Sec. 422.33].

(B) Cord‑and‑Plug‑Connected Ranges. A plug and receptacle of a cord‑and‑plug‑connected household electric range accessible from the front of the range by the removal of a drawer meets the disconnecting means requirements of Sec. 422.33(A).

These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code

About the Author

Mike Holt

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Sign up for our eNewsletters
Get the latest news and updates

Voice Your Opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!