When it comes to the placement of Class 1, Class 2, and Class 3 remote-control, signaling, and power-limited circuits, which one of the following statements meets Code requirements?
- Class 1, Class 2 and Class 3 circuits (in any combination) can occupy the same cable, enclosure, or raceway with other circuits as long as all circuit conductors have the same insulation rating.
- Two or more Class 2 circuits can occupy the same cable, enclosure, or raceway with other circuits.
- Two or more Class 3 circuits can occupy the same cable, enclosure, or raceway with other circuits.
- Class 2 circuits can occupy the same cable, enclosure, or raceway with Class 3 circuits.
Answer: D
As per 725.139, Class 2 and Class 3 remote-control, signaling, and power-limited circuits shall be permitted to occupy the same cable, enclosure, or raceway with other circuits as long as the circuits are Class 2 or Class 3.
Cables and conductors of Class 2 and Class 3 circuits shall not be placed in any cable, cable tray, compartment, enclosure, manhole, outlet box, device box, raceway, or similar fitting with conductors of electric light, power, Class 1, non-power-limited fire alarm circuits, and medium power network-powered broadband communications circuits unless permitted by 725.136(B) through (I).