Question: Are fixed storage type water heaters considered to be a continuous load?
See answer below.
Answer: Yes if 120 gallons or less in capacity.
Reference: Section 422.13
Explanation: The 2023 NEC stated that the branch circuit overcurrent device and conductors were to be sized at 125% of the rating of the water heater. It was unclear if this was the final branch circuit conductors or if it also applied to service and feeder conductors. The new requirement in rhe 2026 NEC clearly makes it a continuous load and will require the appropriate adjustments to feeders and service conductors as well.
Lupacchino is a senior design engineer with Gaylor Electric, Inc. in Noblesville, Ind. and serves as an alternate on NEC Code-Making Panel No. 3. He is currently licensed in more than 80 jurisdictions. He can be reached at [email protected]