Test Your Code IQ — October 2026
How much do you know about the National Electrical Code?
All questions and answers are based on the 2026 NEC.
Q1: Ground-fault circuit-interrupter (GFCI) protection for personnel shall be provided for electric space heating cables installed in electrically heated floors of _____.
a) basements
b) bedrooms
c) dining rooms
d) kitchens
Q2: In general, a non–grounding-type receptacle shall be permitted to be replaced with a(n) _____ type of receptacle.
a) AFCI
b) GFCI
c) locking
d) nonlocking
Q3: Where separate _____ conductors and supply-side bonding jumpers are installed, a terminal bar for all grounding and bonding conductor connections shall be secured inside the transformer enclosure.
a) branch circuit
b) equipment grounding
c) grounding electrode
d) ungrounded
Q4: A neutral conductor that carries only the _____ current from other conductors of the same circuit shall not be required to be counted as a current-carrying conductor when applying the provisions of Sec. 310.15(C)(1).
a) line
b) objectionable
c) phase
d) unbalanced
Q5: Where rigid metal conduit (RMC) enters an enclosure, a bushing shall be provided to protect the wires from _____ unless the box, fitting, or enclosure is designed to provide such protection.
a) abrasion
b) arcing
c) faulting
d) grounding
Q6: Luminaires with open or partially enclosed lamps, pendant luminaires, and _____ shall not be permitted in clothes closets.
a) electric-discharge luminaires
b) lampholders
c) LED luminaires
d) recessed luminaires
Answers:
Q1: d) kitchens
Section 424.44(E) confirms, "GFCI protection shall be provided for cables installed in electrically heated floors of bathrooms and kitchens and hydromassage bathtub locations."
Q2: b) GFCI
According to Sec. 406.12(D)(2)(b), "Non–grounding-type receptacles shall be permitted to be replaced with ground-fault circuit-interrupter-type receptacles."
Q3: b) equipment grounding
Per Sec. 450.12(A)(1): "Where separate equipment grounding conductors and supply-side bonding jumpers are installed, a terminal bar for all grounding and bonding conductor connections shall be secured inside the transformer enclosure."
Q4: d) unbalanced
As stated in Sec. 310.15(E)(2), "A neutral conductor that carries only the unbalanced current from the other conductors of the same circuit shall not be considered current-carrying."
Q5: a) abrasion
Section 344.46 states, "Where a conduit enters a box, fitting, or other enclosure, a bushing shall be provided to protect the wires from abrasion unless the box, fitting, or enclosure is designed to provide such protection."
Q6: b) lampholders
Section 410.16(C) confirms, "Luminaires with open or partially enclosed lamps, pendant luminaires or lampholders shall not be installed."
Ryan Jackson
Ryan Jackson
Ryan Jackson is a National Electrical Code instructor and textbook author in the Salt Lake City, Utah area. He is also a technical consultant for the Steel Tube Institute. He is a member of Code-Making Panels 3 and 17 for the National Electrical Code and serves on several technical committees for UL Standards and Engagement. He is certified as an inspector in electrical, building, mechanical, and plumbing codes, and has taught the NEC and NFPA 70E at the national level over the last three decades.