No Room to Grow

As indicated by these two photos, when PVC thermal expansion and contraction is not taken into consideration when designing and installing PVC conduit runs, the pipe run can simply self-destruct. Section 300.7(B) requires expansion fittings to be used on raceways “where necessary to compensate for thermal expansion and contraction.” Section 352.44 more specifically requires expansion fittings to be used for PVC conduit where the length change for a straight run between securely mounted items is expected to be ¼ in. or greater, in accordance with Table 352.44.

The pipe run in the photo is approximately 30 ft long. If we assume a temperature change from 95°F in the summer to about 5°F in the winter — which happens on a regular basis where I live in New England — then there is a temperature change of 90°F. According to Table 352.44, a 100-ft run would experience a length change of about 3.65 in. Therefore, this 30-ft pipe run would experience a length change of approximately
1 in. If an expansion fitting is not used, this length change will cause more than enough strain and pressure on the couplings, clips, and connectors to cause distortion and breakage. That is exactly what happened to this installation.

This Service Got Ambushed

This job was ambushed by the lack of bushings. Section 300.4 requires insulated conductors sized 4 AWG and larger to be protected by a fitting, such as a plastic bushing, when installed in raceways such as this EMT. Protective bushings are not required for raceways threaded into enclosures where the threaded hubs or bosses provide a smooth rounded edge. The service raceway entering the top of the disconnect is also lacking a bonding bushing as required by 250.92(B). Standard locknuts are not permitted as the only bonding means for bonding a service raceway to an enclosure containing service conductors. Bonding jumpers must be used to bond around “impaired connections,” such as the remaining knockout rings. If a ground fault occurred on the service conductors — and the fault current passed through the small bits of metal connecting the rings together — the rings could simply be blown apart by the high fault current, which could then cause an arc and a fire. The foot lug for the bonding jumper attached to the side of the enclosure was attached to the enclosure with a sheet metal screw. Using sheet metal screws is not one of the methods permitted in Sec. 250.8.

About the Author

Russ LeBlanc

Russ LeBlanc

Owner

Russ started in the electrical trade as an apprentice in 1985. He worked his way up to become a Journeyman Electrician and then eventually became a Master Electrician and Licensed Construction Supervisor. In 1999 Russ become an Electrical Instructor for The Peterson School of Engineering in Massachusetts where he developed his passion for teaching, and quickly became Department Head of Electrical Instruction. Russ has taught thousands of apprentices, electricians, engineers, inspectors, and other electrical professionals during his career as an instructor. He continues to provide electrical professionals with Electrical Code seminars, Arc-Flash Awareness training seminars and educational material through his LeBlanc Consulting Services in North Reading, MA whose specialty is educating electricians. He has been an active member of the NFPA Electrical Section and has authored hundreds of National Electrical Code proposals and comments which have become Code rules to improve the safety for the electrical industry. Russ is also an IAEI certified Electrical Inspector.

Please visit www.russleblanc.net for more information.

Sign up for our eNewsletters
Get the latest news and updates

Voice Your Opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!