Illustrated Catastrophes: Curious Choice of Covers
The type of cover installed on this exterior receptacle was an inappropriate choice by the installer. For 15A and 20A, 125V and 250V receptacles installed in wet locations, Sec. 406.9(B)(1) requires an enclosure that is “weatherproof whether or not the attachment plug cap is inserted.” This cover is obviously not weatherproof right now. This open cover will allow moisture and rain to damage the GFCI receptacle and other components of this circuit. The use of a deeper cover could solve this problem. These types of receptacles are also required to be listed and identified as being weather-resistant where installed in wet locations. Securing that orange extension cord to the building structure was not a good idea either. Doing so created a violation of Sec. 400.12(4). Flexible cords, flexible cables, cord sets (extension cords), and power supply cords are not permitted to be attached to building surfaces. I suppose one could make the argument that Sec. 590.4(J) may permit extension cords to be supported in this manner for temporary installations. The one bit of good news here is the PVC conduit used to wire this receptacle seems to be installed in compliance with Art. 352.
Shocking Find at Marina
I spotted this damaged cord on a recent visit to a local marina. The damage is so severe that the copper conductors are now exposed, which creates a tremendous shock hazard. This cord was used to provide power to a motorized hoist on a pier. Section 555.34(A)(2) permits the use of extra-hard usage portable power cables as permanent wiring on the underside of piers and where flexibility is necessary as on floating piers. However, Sec. 555.34(A)(4) requires the use of rigid metal conduit (RMC), reinforced thermosetting resin conduit (RTRC), or rigid polyvinyl chloride (PVC) conduit to protect wiring above decks of piers and landing stages and below any enclosures it serves. Perhaps using one of those conduits would have been a better choice of wiring methods here. Section 610.11(E) allows suitable cords to be used for wiring of moving parts of hoists if strain relief and protection from physical damage are provided. Section 400.12(7) similarly prohibits using flexible cords, flexible cables, cord sets, and power supply cords where subject to physical damage. Clearly, this cord has been exposed to physical damage and probably should not have been used here. This installation needs immediate repairs to prevent any injuries (or worse) from happening.
Russ LeBlancRuss LeBlanc