Unsafe Conditions When Running Raceway — Part 4
Bonding errors can prove fatal. If your raceway job involves metallic raceway (e.g., EMT, IMC, etc.), then visually inspect and electrically test for bonding violations.
On green construction, bonding errors usually are not a problem. At an existing facility, assume they exist until you can prove otherwise. Adopting this strategy probably saved the lives of two electricians who worked for an industrial electrical services firm. They went to a plant that was new on the client roster. They found dangerous voltage on some existing EMT installations that were directly relevant to their project. Whoever installed the 277V lighting used the raceway as the neutral instead of as the equipment grounding conductor.
If you see ground rods on the load side, then expect dangerous differences of potential to exist between metallic objects. Grounding does not eliminate these, only bonding can. You will have to supply the missing bonding jumpers. Discuss with the project manager whether to install permanent or temporary bonding jumpers. Permanent ones should require customer payment; temporary ones could provide a liability once removed.
Mark LamendolaMark Lamendola