Code Q&A: Using the Neutral Conductor as the Circuit Equipment Grounding Conductor
NEC rules on the neutral conductor as the circuit equipment grounding conductor?
Q. What are the rules in using the neutral conductor for bonding of metal parts?
The neutral conductor can be used as the circuit equipment grounding conductor on the supply side or within the enclosure of the service disconnect in accordance with Sec. 250.24(B) [250.142(A)(1)].
The neutral conductor can be used as the circuit equipment grounding conductor at the source of a separately derived system or within the enclosure of the system disconnecting means in accordance with Sec. 250.30(A)(1) [250.142(A)(3)].
DANGER: Failure to install the system bonding jumper as required by Sec. 250.30(A)(1) creates a condition where dangerous touch voltage from a ground fault won’t be removed.
Except as permitted in Sec. 250.30(A)(1) for separately derived systems and Sec. 250.32(B) Exception for separate buildings/structures, the neutral conductor isn’t permitted to serve as an equipment grounding conductor on the load side of service equipment [250.142(B)].
Exception No. 1: In existing installations, the frames of ranges, wall-mounted ovens, counter-mounted cooking units, and clothes dryers can be connected to the neutral conductor in accordance with Sec. 250.140 Exception.
Exception No. 2: The neutral conductor can be connected to meter socket enclosures on the load side of the service disconnecting means if:
  1. Ground-fault protection isn’t provided on service equipment,
  2. Meter socket enclosures are immediately adjacent to the service disconnecting means, and
  3. The neutral conductor is sized in accordance with Sec. 250.122, based on the ampere rating of the occupancy’s feeder overcurrent device.
Mike Holt
Mike Holt