Code Q&A: Sizing the GEC
NEC guidelines for sizing grounding electrode conductors
Q. What are the Code requirements for sizing the grounding electrode conductor (GEC) at a service to a rod type electrode and concrete-encased electrodes?
A. Metal underground water pipe electrodes and metal in-ground support structures must be sized in accordance with Table 250.66. Other electrodes such as ground rods, concrete-encased electrodes, and ground rings can be sized using Sec. 250.66(A) through (C).
(A) Rod-type grounding electrode. If the GEC or bonding jumper connects to one or more ground rods [250.52(A)(5)] and doesn’t connect to another type of electrode that requires a larger conductor the GEC isn’t required to be larger than 6 AWG copper.
(B) Concrete-encased grounding electrode. If the GEC or bonding jumper is connected to one or more concrete‑encased electrodes [250.52(A)(3)] and doesn’t connect to another type of electrode that requires a larger size conductor, the GEC isn’t required to be larger than 4 AWG copper.
These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visitwww.mikeholt.com/code
Mike Holt
Mike Holt