All questions and answers are based on the 2026 NEC.
Q1: Fill in the blank. The power supply to a mobile home shall be a feeder assembly consisting of not more than one listed _____ mobile home power-supply cord or a permanently installed feeder.
a) 30A
b) 40A
c) 50A
d) 100A
Q2: Fill in the blank. If used to splice service conductors, _____ must be marked “suitable for use on the line side of service equipment” or equivalent.
a) devices for splices and taps
b) power distribution blocks
c) pressure connectors
d) all of these
Q3: Fill in the blank. Aluminum electrical metallic tubing (EMT) shall be provided with approved supplementary corrosion protection where encased in concrete or in direct contact with _____.
a) concrete
b) earth
c) masonry
d) any of these
Q4: Fill in the blank. Where located in a remote location, a transformer disconnecting means shall be _____, and its location shall be field marked on the transformer.
a) accessible only to qualified persons
b) accessible to unqualified persons
c) lockable
d) readily accessible
Q5: Fill in the blank. Disregarding the exception, the smallest copper overhead service conductors allowed for a service are _____ AWG.
a) 8
b) 6
c) 4
d) 2
Q6: Which of these methods is allowed for identifying grounded conductors 6 AWG and smaller?
a) gray outer finish
b) white outer finish
c) white outer finish with a tracer thread
d) any of these
Answers:
Q1: c) 50A
According to Sec. 550.10(A), "The power supply to the mobile home shall consist of not more than one listed 50A mobile home feeder assembly or a permanently installed feeder."
Q2: d) all of these
Section 230.46 requires that devices for splices and taps, power distribution blocks, and pressure connectors shall "be marked or identified as “suitable for use on the line side of service equipment” or equivalent."
Q3: b) earth
Per Sec. 358.10(B)(2): "Aluminum EMT shall be provided with approved supplementary corrosion protection where encased in concrete or in direct contact with the earth."
Q4: c) lockable
Section 450.16 states, "Where located in a remote location, the disconnecting means shall be lockable open in accordance with Sec. 110.25, and its location shall be field marked on the transformer."
Q5: a) 8
According to Sec. 230.23(B), "The conductors shall not be smaller than 8 AWG copper or 6 AWG aluminum or copper-clad aluminum."
Q6: d) any of these
Section 200.7(A) lists gray outer finish, white outer finish, and white outer finish with a tracer thread as permittable means for identifying grounded conductors 6 AWG and smaller.
Ryan JacksonRyan Jackson
Ryan Jackson is a National Electrical Code instructor and textbook author in the Salt Lake City, Utah area. He is also a technical consultant for the Steel Tube Institute. He is a member of Code-Making Panels 3 and 17 for the National Electrical Code and serves on several technical committees for UL Standards and Engagement. He is certified as an inspector in electrical, building, mechanical, and plumbing codes, and has taught the NEC and NFPA 70E at the national level over the last three decades.